I own one of those licenses sprinkler contractor companies you referenced
and I worked for FM Global for 14 years. I did not mean to suggest the fire
department inspectors should conduct the inspections. In most states, these
guys are the ones who have been assigned the task of enforcing the law. They
visit facilities to ensure the inspections are performed by a certified fire
protection contractor on an annual basis in addition to many other
responsibilities. 

 

Inspections completed by the insurance company representatives and/or site
safety personnel do not meet State Law in Georgia or many other states which
I have investigated. Georgia State Law clearly states that all water based
fire protection systems shall be inspected in accordance with NFPA 25 by a
certified fire protection contractor on an annual basis AND that the
inspection tag shall be maintained at the base of the sprinkler system riser
for each system. These minimum annual inspections by fire protection
contractors are required even if inspections are performed by insurance
company representatives and/or employees at the location. The Georgia Fire
Sprinkler Act specifically states "Fire protection system inspector" means
an individual who performs inspections only on water-based fire protection
systems in accordance with applicable codes and standards as adopted by the
Commissioner. Such term does not apply to state, local, and insurance
inspectors while acting in their official capacities.

 

My brother is a 19 year fire fighter and I am very aware of the limited
resources they have regarding inspectors. I was simply suggesting a process
which might help them identify locations which are not following the state
law.

 

Maybe this clarifies my comments.

 

 

Date: Thu, 26 Mar 2009 09:15:23 -0600

From: <[email protected]>

Subject: RE: Concurrent Testing

To: <[email protected]>

Message-ID:

      <[email protected]>

Content-Type: text/plain; charset="us-ascii"

 

State fire marshal and local fire departments do not have the manpower to
inspect all the facilities on a regular basis.  That is why they depend on
the owner to employ a licensed contractor to do the inspection and then
submit the reports.   One jurisdiction we dealt with recently stated it
would take 3 years to inspect the major facilities within their
jurisdiction, that doesn't include the "less significant" occupancies.  They
don't have the funding to hire more people and they are very limited on
resources.  

 

Many of the larger commercial or industrial facilities have inspections
performed by their insurance underwriter or their site safety personnel.
They don't leave inspection tags and unless you ask for their report, the
owner isn't going to share it with you.  He might not share it with you even
if you do ask.  So just because there's not a tag you can't always assume
there have been no inspections.  

 

 

Craig L. Prahl, CET   

Fire Protection Specialist

Mechanical Department

CH2MHILL

Lockwood Greene

1500 International Drive

PO Box 491, Spartanburg, SC  29304-0491

Direct - 864.599.4102

Fax - 864.599.8439

[email protected]

http://www.ch2m.com <http://www.ch2m.com/>  

 

 

 

 

-----Original Message-----

From: [email protected]

[mailto:[email protected]] On Behalf Of Rodney Hamm

Sent: Wednesday, March 25, 2009 7:35 PM

To: [email protected]

Subject: Re: Concurrent Testing

 

 

..................

 

 

I will add one additional point...the enforcement of these requirements
should improve. We have a problem in Georgia anyway, I wonder if the problem
is nationwide? I have visited way too many facilities in Georgia and
throughout the Southeastern United States which have expired inspection tags
and there area a significant percentage of locations which have NEVER even
had an inspection completed by a certified sprinkler contractor or a
certified alarm company. The larger commercial facilities (likelihood of a
more severe fire incident in many instances) located in the smaller towns
and/or outside of city limits are more likely to have this problem than the
smaller facilities. Seems like the fire department inspectors do not visit
or do not ask about fire inspections at the larger facilities; based on my
experience, inspections are warranted MUCH more at these facilities than
most of the smaller locations. I am generally against government regulation,
but maybe each state should consider a copy of the current fire inspection
forms to verify inspections have been performed by a certified sprinkler
contractor and a certified fire alarm company prior to issuing the annual
business license or possibly some other annual renewal. If the company does
not provide the required verification, send the fire department inspectors
out for a quick visit to discuss the issue. The fact that it is required to
obtain the annual business license would probably be enough incentive for
most companies.

 

 

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to