That this room occurs in a residence doesn't change the fact that it's an R-3 occupany and a 13D system, so the intent is still a life safety appraoch. I would use QR SSP or SSU sprinklers with a K-factor as closely matched as possible to the one you select for the residential sprinklers. If the mechanical room is the hydraulically remote area, you could do a calc at .05.
My opinion only, Steve Leyton PD&C Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Todd Williams" <[email protected]> Date: Mon, 6 Apr 2009 14:49:05 To: <[email protected]> Subject: 13D in large res mech space I am working on a large single family house with a mechanical room that is 564 sqft. The ceiling is open to the wood trusses and there are lots of ducts and wiring in the space. No smooth ceiling and residential pendent sprinklers cannot be installed with their listing or Code. There are probably going to be 5 or 6 sprinklers in the room. My thought was to use QR uprights because nothing else will work. Does this make sense? What would be the appropriate design criteria? The water supply is a 13D pump and tank. This is a partial system that is not required by Code and the AHJ could care less what goes on. He doesn't even want to see the plans. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)