In addition to using QR heads, you'll be able to use 200'F. We've seen a lot of "Mech. rooms" where the 155/175'f residential heads were not 50'f above room temp.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Monday, April 06, 2009 3:49 PM To: [email protected] Subject: 13D in large res mech space I am working on a large single family house with a mechanical room that is 564 sqft. The ceiling is open to the wood trusses and there are lots of ducts and wiring in the space. No smooth ceiling and residential pendent sprinklers cannot be installed with their listing or Code. There are probably going to be 5 or 6 sprinklers in the room. My thought was to use QR uprights because nothing else will work. Does this make sense? What would be the appropriate design criteria? The water supply is a 13D pump and tank. This is a partial system that is not required by Code and the AHJ could care less what goes on. He doesn't even want to see the plans. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)