The 250# is also for permanence and durability.  During and after installation, 
people grab the pipe to balance themselves, move scaffolding, do pull-ups etc.  
Even if the "tie off" justification were refuted in a proposal to remove the 
250#, the TC would still keep it.  

J. Scott Mitchell, P.E.

--- On Fri, 4/10/09, Thom McMahon <[email protected]> wrote:

From: Thom McMahon <[email protected]>
Subject: RE: Hangers vs. structure to hang from
To: [email protected]
Date: Friday, April 10, 2009, 3:02 PM

I would give them the "Actual" weight of the water filled pipe, and just
note that your hanger materials shall be in accordance with chapter 9 NFPA
13. The structural safety factors and point loads are the structural
engineers responsibility.


Just a adjunct to your question, Why do we have to allow the weight of the
pipe + 250# (Weight of average fitter?) to our loads, when OSHA doesn't
allow tie off to anything but the structure, and that has to handle impact
loads of over 3000#? Isn't someone just as likely to tie off to a 1/2"
insulated copper water line as to our pipe, if they're not following OSHA to
begin with?