"AHJ's like them (with cause) so they require them"

Not so fast Cerberus............

The AHJ's enforce the code section, that doesn't mean we like or agree with
it.

Personally I prefer 2-1/2 NH. Why because just about everyone's got it (yep
it's the same hose used for handlines), it's easy to handle (as a
driver/operator I've been the one to make the connection and a John J
pointed out you have two lines supplying the FDC (could be serving a
standpipe right) so there's some redundancy (yes even if we lose hydrant
water we still have something in the booster tank if only for mere minutes).


John Drucker
Fire Protection Subcode Official
New Jersey 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, April 10, 2009 2:17 PM
To: [email protected]
Subject: Re: stortz and UL listing

Folks in hell want ice water but that doesn't mean they get it.  I  
just looked through the UL Directory and did not find one. May have  
overlooked it but until proven otherwise, yes give me a cup of that  
fine boiling water please.

As for HOW can that be.  The AHJ's like them (with cause) so they  
require them.  Tukwila has created a conflict by wanting ice water.

Roland

On Apr 10, 2009, at 6:56 AM, [email protected] wrote:

> well,
>
> There must be one Stortz UL listed because it is spec's by the  
> following
> agency: _http://www.ci.tukwila.wa.us/pubwks/standards/Water/WS-15.pdf_
> (http://www.ci.tukwila.wa.us/pubwks/standards/Water/WS-15.pdf)
> They require UL Listed Stortz.
> Now, since it is part of the fire sprinkler system is it not  
> required to be
> UL Listed? (per NFPA 13)
>
> Forest  Wilson
>
> Project Manager
> Cherokee Fire Protection Co.
> 3195  Dayton Xenia Rd Ste 900
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to