You might want to take a look at Table A.5.6.3 (NFPA 13 2002) under 
plastic containers. If it is a non-combustible liquid, I would think 
this would apply. Check the MSDS for what is being stored in the IBC.



At 09:59 AM 4/24/2009, you wrote:
>Flammability is a 1 yet you say it's a non-combustible?
>
>What is the flash point?  What is the chemical?
>
>I believe the consensus here was to protect these types of 
>arrangements based on Group A plastics.  Also consider the 
>possibility of empty containers being present.  There is some 
>discussion concerning the actual hazard present with containers such 
>as this when filled with non-combustible contents but I don't recall 
>seeing any hard fast rulings or design criteria based on such.
>
>
>
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>PO Box 491, Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Lori Kitchen
>Sent: Friday, April 24, 2009 9:58 AM
>To: [email protected]
>Subject: Intermediate Bulk Containers
>
>We have been asked to sprinkler a warehouse that will store 
>intermediate bulk containers (IBC) containing a non-combustible 
>liquid.  They are made of high density polyethylene.  MSDS says the 
>flammability is a 1 however we normally treat polyethylene as a 
>Group A plastic.  Has anyone designed a system for this type of container?
>
>
>
>I appreciate the input.
>
>
>
>
>
>Lori Kitchen
>
>VP, Service & Maintenence Division
>
>Whitewater Fire Sprinkler
>
>
>
>316-295-4120 (office)
>
>316-295-4162 (fax)
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to