I wouldn't let them relocate any heads without a new underground plan, flow test, hydraulic calculations, seismic bracing, FDC, backflow, gauge and maybe a pump and some new windows. Some contractors think they can get away with anything just because the occupancy and use hasn't changed and there is no requirement to meet current code.
Happy Friday. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ 85024 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of å... .... Sent: Friday, May 08, 2009 10:10 AM To: [email protected] Subject: review of sprinkler plans ends up with GC requesting the reviewer to provide additional plan sheet because contractor don´t want to Am reviewing a drawing set for a medical outpatient facility where sprinkler contractor is doing a retrofit: changing out armovers and over 200 sprinkler heads I asked the sprinkler contractor to A. provide a sheet with information that included enough of the site underground to: tell if the UG was fed by a loop or dead end, location and dimension of underground pipe location and specs on FDC and BFP, where the gauge and flow hydrants were elevation of the same and finished floor include the new waterflow test derate the HC coefficient for existing mains that are to remain in place B. and the sprinkler contractor was asked to brace the existing mains per 2007 NFPA 13. sprinkler contractor refuses to do the above, and GC wants me to draw up the site plan showing UG, because this internationally recognized sprinkler company, simply will take too long and the GC wants the job done. Sprinkler contractor is probably saying it is not in their bid and scope of work, but I don´t see where in NFPA 13, that it is NOT in their scope of work. Am I wrong, dead wrong, or kinda wrong. scot deal excelsior fire _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)