Yes, as a matter of fact we're doing a small addition to a dorm where the existing building is designed to 13R for the two wings, 13 for the center section housing Campus Security's office (incidental use if you stretch a little), and a daycare (likely NOT for the college students at this ritzy alma mater, and thus NOT incidental use). They first spec'd 13 for the center section and I pointed out that the seminar room, living room/lounge, and common area in the addition were exactly the incidental use 13R addresses in areas outside the dwelling unit, and they allowed it, although the responsibility for dealing with the new 3rd party AHJ is mine, as if he's got 3 eyes and horns. Hey, it's the state code, I understand it, and if he needs help understanding it, I'll be the first to offer assistance.
So NO this is not correct, and they'd need a horizontal separation equal to what building separation would need in order to apply two codes. But it happens a lot more often than it should. If they resist you pointing out the fact that 13 should apply to the entire building, maybe point out that using their logic, you could do the top 4 floors of a residential high-rise using 13R? IF the insist you do it their way, and the AHJ is agreeable, get everyone to sign a Memo of Understanding and take responsibility for whatever events may occur (including death) and design it their way. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Thursday, May 28, 2009 7:44 AM To: [email protected] Subject: 13 & 13R - same building I know this has been bantered around before, but I am still a little confused. I have been asked to quote a building where the 1st floor is a church and the upper 2 floors are apartments. The spec calls for the 1st floor to be 13 and the upper floors 13R. To me this doesn't make sense since 13 is a property standard and 13R is life safety. Is there any situation where this is allowed? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)