And even if its not because it meets the criteria for omission of
sprinklers, there's that nasty little 3,000 SF min MRA to deal with.
In a bid a week ago we included the heads below the floor cause it was
cheaper to sprinkler it than have a 3,000 sf MRA!

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, June 01, 2009 8:30 AM
To: [email protected]
Subject: Re: Combustible rated floors

Is there a 1 hour rated ceiling below the truss and a 1 hour rated 
floor above the truss? What is the truss spacing? Are they made with 
fire retardant lumber? If it doesn't meet any on the exceptions in 
8.14, then it should be sprinklered. Are the AHJs accepting this?



At 07:56 AM 6/1/2009, you wrote:
>We have a growing trend up here in which contractors are not installing
>sprinklers in combustible floor spaces (open wood truss) simply because
>there is a 1hr rated floor and ceiling assembly which sandwiches the
>combustible space.  We have been including sprinklers for these areas in
>our bids but have been loosing work because of this.  Am I missing
>something and can sprinklers be omitted?
>Thanks,
>Dewayne Martinez
>Design Build Fire Protection
>New Berlin, WI
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to