it s worth a small amount f time to ensure the AHJ is aware of when  
protection can be omitted and when the 3,000SF remote area is  
applicable.

Roland

On Jun 1, 2009, at 6:02 AM, Dewayne Martinez wrote:

> 1hr ceiling attached to the bottom of the truss and a 1hr floor on  
> top.
> Truss are normally 16 or 24in OC.
> No flame retardant material in the truss construction. So far, we have
> lost jobs in 2 municipalities where the
> AHJ has accepted this.  I have been telling my salesmen that is is not
> worth the liability to omit these sprinklers
> and to keep them in our bid.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Monday, June 01, 2009 7:30 AM
> To: [email protected]
> Subject: Re: Combustible rated floors
>
> Is there a 1 hour rated ceiling below the truss and a 1 hour rated  
> floor
> above the truss? What is the truss spacing? Are they made with fire
> retardant lumber? If it doesn't meet any on the exceptions in 8.14,  
> then
> it should be sprinklered. Are the AHJs accepting this?