At 09:02 AM 6/1/2009, you wrote:
>1hr ceiling attached to the bottom of the truss and a 1hr floor on top.
>Truss are normally 16 or 24in OC.
>No flame retardant material in the truss construction. So far, we have
>lost jobs in 2 municipalities where the
>AHJ has accepted this.  I have been telling my salesmen that is is not
>worth the liability to omit these sprinklers
>and to keep them in our bid.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
>Williams
>Sent: Monday, June 01, 2009 7:30 AM
>To: [email protected]
>Subject: Re: Combustible rated floors
>
>Is there a 1 hour rated ceiling below the truss and a 1 hour rated floor
>above the truss? What is the truss spacing? Are they made with fire
>retardant lumber? If it doesn't meet any on the exceptions in 8.14, then
>it should be sprinklered. Are the AHJs accepting this?
>
>
>
>At 07:56 AM 6/1/2009, you wrote:
> >We have a growing trend up here in which contractors are not installing
>
> >sprinklers in combustible floor spaces (open wood truss) simply because
>
> >there is a 1hr rated floor and ceiling assembly which sandwiches the
> >combustible space.  We have been including sprinklers for these areas
> >in our bids but have been loosing work because of this.  Am I missing
> >something and can sprinklers be omitted?
> >Thanks,
> >Dewayne Martinez
> >Design Build Fire Protection
> >New Berlin, WI
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to:
> >[email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to