NFPA 70 only says that "by special permission, smaller working spaces shall be permitted where all exposed live parts operate at not greater than 30 volts rms, 42 volts peak, or 60 volts dc." NFPA 70, 110.26(A)(1)(b) But that has nothing to do with location of pipes.
The rules for the Dedicated Electrical Space under sub-paragraph (F) of the same section give no special allowances for low voltage versus other voltage systems. In Chapter 8 dealing with Communications Circuits, installation is to comply with section 110.3(B) [800.18] 110.3(B) "Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling." It appears that the same rules apply for all electrical spaces regardless of voltage. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Tuesday, June 09, 2009 8:27 AM To: [email protected] Subject: Low voltage electrical rooms Is there any clearance requirements in low voltage electrical rooms (telecommunication / data) between the sprinkler pipe and the equipment? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)