The UFC actually requires wet pipe sprinkler protection in data and computer
centers.  That was quite a shock to the comm squadron on my base when I told
them to put back a wet pipe system in a server room that they had deleted
without asking anyone.

On Tue, Jun 9, 2009 at 4:22 PM, <[email protected]> wrote:

> Be cautious in quickly deciding to omit sprinklers in these types of rooms.
>
> While there may be allowances permitted by code to omit the sprinklers
> there needs to be some analysis and discussion with the owner on just what
> impact a fire within one of these spaces can have on their operation.
>
> Loss of communications whether by phone, data or other means can be
> devastating to a company.  The extent of loss within these rooms in a fire
> is almost always 100%.  Electronic equipment is temperature sensitive so
> even if it was not directly burned, the elevated temperature can destroy it.
>  Not to mention the repair of cabling within and to a point beyond the room.
>
> Having discussions with clients whose original fear was the equipment
> getting wet and who have had total losses due to even small fires within the
> rooms, their follow-up choice was to provide sprinklers.
>
> Remember that even if the equipment did get wet accidentally, it can be
> dried out, and restored to service a lot faster than it can had it been
> exposed to a fire.  And also don't forget that these rooms end up being
> storage closets for miscellaneous junk sooner or later.
>
> We should make sure the choices made are in the overall best interest of
> the clients we serve.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Haji, Jaber M
> Sent: Tuesday, June 09, 2009 8:31 AM
> To: [email protected]
> Subject: RE: Low voltage electrical rooms
>
> You may use the exception item to delete the AS from such rooms .
>
> Jaber M. Al-Haji
> Loss Prevention Dept
> KAS,
> [email protected]
> [email protected]
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Dewayne Martinez
> Sent: Tuesday, June 09, 2009 3:27 PM
> To: [email protected]
> Subject: Low voltage electrical rooms
>
> Is there any clearance requirements in low voltage electrical rooms
> (telecommunication / data) between the sprinkler pipe and the equipment?
>
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> The contents of this email, including all related responses, files and
> attachments transmitted with it (collectively referred to as "this Email"),
> are intended solely for the use of the individual/entity to whom/which they
> are addressed, and may contain confidential and/or legally privileged
> information. This Email may not be disclosed or forwarded to anyone else
> without authorization from the originator of this Email. If you have
> received this Email in error, please notify the sender immediately and
> delete all copies from your system. Please note that the views or opinions
> presented in this Email are those of the author and may not necessarily
> represent those of Saudi Aramco. The recipient should check this Email and
> any attachments for the presence of any viruses. Saudi Aramco accepts no
> liability for any damage caused by any virus/error transmitted by this
> Email.
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to