Not an obstruction because you are not trying to throw over it.  

I wouldn't get torn up about 24" deep with 0"-17" clear above for the same
reasoning. But I agree at some point perhaps a little judgment is in order?


So what about a 7' deep shelf unit all the way to the ceiling (or a couple
inches from the ceiling) and heads 7'6" off the wall.  A 12" shelf in an
office is probably LH.  7' deep and it's probably OH at least.  Let assume
the density is right what ever it is.  That one I don't have as clear an
answer.  Can't think of a code reason it's wrong but it feels wrong.  Short
of some code section I'd have to go along with it.    

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Friday, June 12, 2009 9:56 AM
To: [email protected]
Subject: Book cases or cabinets against a wall. Are they Obstructions?

Forum members,

 

I've drilled the 18" clearance issue into a building owners head and know
he's got me scratching my head with a situation at his facility.

He has a bookcase against a wall that is 12" deep with a clear space of
about 6" above between the ceiling and the top of the bookcase. The
sprinkler is 6" out in front of the bookcase. He's asking me why the
bookcase is not an obstruction. 

It's Friday after a long week and I'm not sure why the book case is not an
obstruction.

 

What if the geometry was different? Let's say a cabinet that 24" deep and
had 17" clearance between top of cabinet and ceiling?

 

If you could point me to the right code sections, I would appreciate it. I
have looked at supplement 7 in the residential handbook but this is an
office building with standard spray sprinklers. 

 

Thanks for any help you can give,

 

Randy Knutson

Shilo Automatic Sprinkler, Inc.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to