Randy, Thom and Chris are all over this one. just check out the annex material that the Committee provides to indicate the intent here. "A.8.6.6 The 18 in. dimension is not intended to limit the height of shelving on a wall or shelving against a wall in accordance with 8.6.6. Where shelving is installed on a wall and is not directly below sprinklers, the shelves, including storage thereon, can extend above the level of a plane located 18 in. (457 mm) below ceiling sprinkler deflectors. Shelving, and any storage thereon, directly below the sprinklers cannot extend above a plane located 18 in. below the ceiling sprinkler deflectors."
So ease up... and stop screamin' at the owner so much. :) Besides it's Friday man! It should be recognized that the above is my opinion as a member of the NFPA 13 Committee on Installation Criteria representing the NFSA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFSA nor the NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 845-878-4200 x138 www.sprinkleracademy.com ---------------------------------------- > From: [email protected] > To: [email protected] > Subject: RE: Book cases or cabinets against a wall. Are they Obstructions? > Date: Fri, 12 Jun 2009 13:59:24 -0600 > > 8.6.6.1 sets the 18" from top of storage to deflector, but the handbook FAQ > "Do the requirements of 8.6.6.1 apply to shelving against the wall? > "Sprinklers installed near wall mounted shelves or piled storage located > against a wall are not intended to be governed by the requirements of > 8.6.6.1" > > Thom McMahon, SET > Firetech, Inc. > 2560 Copper Ridge Dr > P.O. Box 882136 > Steamboat Springs, CO 80488 > Tel: 970-879-7952 > Fax: 970-879-7926 > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Chris Cahill > Sent: Friday, June 12, 2009 9:21 AM > To: [email protected] > Subject: RE: Book cases or cabinets against a wall. Are they Obstructions? > > Not an obstruction because you are not trying to throw over it. > > I wouldn't get torn up about 24" deep with 0"-17" clear above for the same > reasoning. But I agree at some point perhaps a little judgment is in order? > > > So what about a 7' deep shelf unit all the way to the ceiling (or a couple > inches from the ceiling) and heads 7'6" off the wall. A 12" shelf in an > office is probably LH. 7' deep and it's probably OH at least. Let assume > the density is right what ever it is. That one I don't have as clear an > answer. Can't think of a code reason it's wrong but it feels wrong. Short > of some code section I'd have to go along with it. > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Randy Knutson > Sent: Friday, June 12, 2009 9:56 AM > To: [email protected] > Subject: Book cases or cabinets against a wall. Are they Obstructions? > > Forum members, > > > > I've drilled the 18" clearance issue into a building owners head and know > he's got me scratching my head with a situation at his facility. > > He has a bookcase against a wall that is 12" deep with a clear space of > about 6" above between the ceiling and the top of the bookcase. The > sprinkler is 6" out in front of the bookcase. He's asking me why the > bookcase is not an obstruction. > > It's Friday after a long week and I'm not sure why the book case is not an > obstruction. > > > > What if the geometry was different? Let's say a cabinet that 24" deep and > had 17" clearance between top of cabinet and ceiling? > > > > If you could point me to the right code sections, I would appreciate it. I > have looked at supplement 7 in the residential handbook but this is an > office building with standard spray sprinklers. > > > > Thanks for any help you can give, > > > > Randy Knutson > > Shilo Automatic Sprinkler, Inc. > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)