13D 1987 as set forth in the 1989 handbook, 4-1.2 Number of design
sprinklers. The number of DESIGN SPRINKLER'S shall include all sprinklers
within a compartment to a maximum of two sprinklers.

The commentary continues "-----It should be clarified that even if more than
two sprinklers are required for coverage in a compartment having a flat
ceiling, the maximum number of sprinklers included as the number of design
sprinklers for water supply calculations is two.-----"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike Cabral
Sent: Thursday, June 18, 2009 12:06 PM
To: [email protected]
Subject: 13D Question 1988 Edition

I have an AHJ that is telling a designer that there can not be 4 sprinklers
in a single compartment. I was told that he is working off an old standard
from 1988 or so. Anyone have recollection of this. 

Mike Cabral