Again, going from memory as well. Isn't / Wasn't there something saying that you need to use the fewest number of sprinklers able to protect the area. So, if you have a 20'x30' room, you need to use 2 sprinklers at 20'x20' spacing, instead of using 4 at 16'x16'. Using 2 sprinklers, you are calculating flowing 40 gallons for the 2 sprinklers vs 26 gallons for 2 sprinklers with 4 heads in the room, both scenarios protecting the same space. Is that possibly what he is referring to?
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Thursday, June 18, 2009 12:36 PM To: [email protected] Subject: RE: 13D Question 1988 Edition Mike, Going from memory, I don't have any standards with me, there is a requirement for QR sprinklers not exceeding 4. I believe that this is actually a 13R requirement though. Maybe this is the confussion. Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Cabral Sent: Thursday, June 18, 2009 12:06 PM To: [email protected] Subject: 13D Question 1988 Edition I have an AHJ that is telling a designer that there can not be 4 sprinklers in a single compartment. I was told that he is working off an old standard from 1988 or so. Anyone have recollection of this. Mike Cabral _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ NOD32 4168 (20090618) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)