Can I apply that to an ESFR warehouse? We'd clean up- 200,000 SF per head? glc
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bryan Dann Sent: Thursday, June 18, 2009 2:23 PM To: [email protected] Subject: RE: 13D Question 1988 Edition I have 1984 13D, it still states "number of design sprinklers shall include all sprinklers within compartment to a maxium of 2 sprinklers". Based on his thinking you don't provide proper coverage? Only two or three heads per compartment no matter how big the compartment is? Have him show you in the book. Bryan A. Dann Dannba Design Services, LLC Fire Sprinkler Designs Office: (740) 363-5878 Cell: (740) 803-0967 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Cabral Sent: Thursday, June 18, 2009 2:06 PM To: [email protected] Subject: 13D Question 1988 Edition I have an AHJ that is telling a designer that there can not be 4 sprinklers in a single compartment. I was told that he is working off an old standard from 1988 or so. Anyone have recollection of this. Mike Cabral _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)