If my calculations are correct it should be a .43/2000 density.

Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Arthur Tiroly
Sent: Monday, June 29, 2009 2:43 PM
To: [email protected]
Subject: RE: In-rack fireprotection

I BELIEVE THAT IS CORRECT.


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay White
Sent: Monday, June 29, 2009 3:33 PM
To: [email protected]
Subject: RE: In-rack fireprotection

I am guessing this is a point or density between the density at 4ft. and the
density of 8ft. wide aisle?

Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay White
Sent: Monday, June 29, 2009 2:30 PM
To: [email protected]
Subject: In-rack fireprotection

In NFPA 13 2002 edition, section 12.3.2.1.2.1; for aisle widths between 4ft
and 8 ft, a direct linear interpolation between densities shall be made. Can
someone explain this?

Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to