Yup, you got it. For example if you look at Figure 12.3.2.1.2(g) if you used Curve "A" with an 8ft aisle at .39/2000 and Curve "C" with a 4ft aisle at .475/2000, a 6ft aisle would give you a density of 0.4325/2000.
And I would hold that density tightly to that 0.4325, I wouldn't let any old contractor get away with only giving 0.43 when the spec says 0.4325 gpm/sq. ft. Specs is specs! ;) Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jay White Sent: Monday, June 29, 2009 3:33 PM To: [email protected] Subject: RE: In-rack fireprotection I am guessing this is a point or density between the density at 4ft. and the density of 8ft. wide aisle? Jay White Estimator/Design Manager Dynamic Fire Protection 1807 Hwy. 25 South Starkville, MS 39759 Phone: 662-324-1550 Fax: 662-324-1545 Cell: 662-312-2426 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jay White Sent: Monday, June 29, 2009 2:30 PM To: [email protected] Subject: In-rack fireprotection In NFPA 13 2002 edition, section 12.3.2.1.2.1; for aisle widths between 4ft and 8 ft, a direct linear interpolation between densities shall be made. Can someone explain this? Jay White Estimator/Design Manager Dynamic Fire Protection 1807 Hwy. 25 South Starkville, MS 39759 Phone: 662-324-1550 Fax: 662-324-1545 Cell: 662-312-2426 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)