All right them. friends again.

On Mon, Jun 29, 2009 at 2:06 PM, <[email protected]> wrote:
> Ok, so maybe I'd cut him just a little slack. ;)
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Monday, June 29, 2009 4:40 PM
> To: [email protected]
> Subject: Re: In-rack fireprotection
>
> Craig,
>
> You've moved out of the range of significant numbers, You can't have a degree 
> of precision in your results that is more precise than you inputs. I'd let 
> him have 0.433.
>
> On Mon, Jun 29, 2009 at 12:57 PM, <[email protected]> wrote:
>> Yup, you got it.  For example if you look at Figure 12.3.2.1.2(g) if you 
>> used Curve "A" with an 8ft aisle at .39/2000 and Curve "C" with a 4ft aisle 
>> at .475/2000, a 6ft aisle would give you a density of 0.4325/2000.
>>
>> And I would hold that density tightly to that 0.4325, I wouldn't let
>> any old contractor get away with only giving 0.43 when the spec says
>> 0.4325 gpm/sq. ft.   Specs is specs! ;)
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
>> 864.599.8439 [email protected] http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Jay
>> White
>> Sent: Monday, June 29, 2009 3:33 PM
>> To: [email protected]
>> Subject: RE: In-rack fireprotection
>>
>> I am guessing this is a point or density between the density at 4ft. and the 
>> density of 8ft. wide aisle?
>>
>> Jay White
>> Estimator/Design Manager
>> Dynamic Fire Protection
>> 1807 Hwy. 25 South
>> Starkville, MS 39759
>> Phone: 662-324-1550
>> Fax:       662-324-1545
>> Cell:      662-312-2426
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Jay
>> White
>> Sent: Monday, June 29, 2009 2:30 PM
>> To: [email protected]
>> Subject: In-rack fireprotection
>>
>> In NFPA 13 2002 edition, section 12.3.2.1.2.1; for aisle widths between 4ft 
>> and 8 ft, a direct linear interpolation between densities shall be made. Can 
>> someone explain this?
>>
>> Jay White
>> Estimator/Design Manager
>> Dynamic Fire Protection
>> 1807 Hwy. 25 South
>> Starkville, MS 39759
>> Phone: 662-324-1550
>> Fax:       662-324-1545
>> Cell:      662-312-2426
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to:
>> [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to