I was going to say that at well BUT, since they are free standing and can be 
moved, if relocated, the sprinkler spacing pattern could be made ineffective or 
non-compliant.  How could you space sprinklers based on a potentially changing 
"wall" layout?

If there is a distinct possibility that these panels can be rearranged, and in 
order to be able to provide a sprinkler layout that would be fixed for the open 
space I would inform the tenant that the height of the partitions needs to be 
lowered to allow a clearance of at least 18"-24" below the ceiling.

Panels at 7'-6" would help with sprinkler issues and would probably be of 
benefit to the HVAC distribution as well.  

Otherwise install 4ft flexheads (or equal) so that they can be moved around to 
accommodate any changes in position of the panels.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thomas Watt
Sent: Wednesday, July 15, 2009 7:13 PM
To: [email protected]
Subject: free standing partitions

Scott,
    I assume you meant 8'-10" partitions, if so, not being 18" below ceiling 
they are an obstruction. So, I would say sprinkler both sides being careful to 
remain at least 6'-0" apart and maintaining 130 sq. ft. per head.

Just my $.02

Thomas Watt



Could someone please help me with this question?
How would pendant sprinklers be located around a free standing partition in a 
ordinary hazard occupancy? The NFPA only seems to address this for light 
hazard.I have 8"-10" partitions in an area with a 9'-6" ceiling in a "mall 
store".
Any input would be helpful.

Scott Enides
S.R.I. Fire Sprinkler LLC
Email: [email protected]   
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to