Or space the heads 8' x 8', calc to 15'x15', and tell them they need to keep walls a minimum of 6" off the heads....nice COR :)
glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, July 16, 2009 8:31 AM To: [email protected] Subject: RE: free standing partitions I was going to say that at well BUT, since they are free standing and can be moved, if relocated, the sprinkler spacing pattern could be made ineffective or non-compliant. How could you space sprinklers based on a potentially changing "wall" layout? If there is a distinct possibility that these panels can be rearranged, and in order to be able to provide a sprinkler layout that would be fixed for the open space I would inform the tenant that the height of the partitions needs to be lowered to allow a clearance of at least 18"-24" below the ceiling. Panels at 7'-6" would help with sprinkler issues and would probably be of benefit to the HVAC distribution as well. Otherwise install 4ft flexheads (or equal) so that they can be moved around to accommodate any changes in position of the panels. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)