Or space the heads 8' x 8', calc to 15'x15', and tell them they need to keep
walls a minimum of 6" off the heads....nice COR :)

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, July 16, 2009 8:31 AM
To: [email protected]
Subject: RE: free standing partitions

I was going to say that at well BUT, since they are free standing and can be
moved, if relocated, the sprinkler spacing pattern could be made ineffective
or non-compliant.  How could you space sprinklers based on a potentially
changing "wall" layout?

If there is a distinct possibility that these panels can be rearranged, and
in order to be able to provide a sprinkler layout that would be fixed for
the open space I would inform the tenant that the height of the partitions
needs to be lowered to allow a clearance of at least 18"-24" below the
ceiling.

Panels at 7'-6" would help with sprinkler issues and would probably be of
benefit to the HVAC distribution as well.  

Otherwise install 4ft flexheads (or equal) so that they can be moved around
to accommodate any changes in position of the panels.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to