Scott,
I assume you meant 8'-10" partitions, if so, not being 18" below ceiling
they are an obstruction. So, I would say sprinkler both sides being careful to
remain at least 6'-0" apart and maintaining 130 sq. ft. per head.
Just my $.02
Thomas Watt
Could someone please help me with this question?
How would pendant sprinklers be located around a free standing partition in
a ordinary hazard occupancy? The NFPA only seems to address this for light
hazard.I have 8"-10" partitions in an area with a 9'-6" ceiling in a "mall
store".
Any input would be helpful.
Scott Enides
S.R.I. Fire Sprinkler LLC
Email: [email protected]