My understanding would be:
NFPA 13, 2007, 11.2.3.3.5 (2) would allow 8' wide with a 8" lintel for light
hazard Room design to be considered an unprotected opening. i.e. you could
still use room design but would have to calc your 'design room' and 2
sprinklers in each of the communicating spaces (that have unprotected
openings). If the door into the other room on the 3rd floor could be
considered 'Non-rated automatic or self closing doors' as stated in NFPA 13,
2007 section 11.2.3.3.5 (1), had your 8" lintel opening (opening restricted
to 8' wide), you could calc the sprinklers in the design room and 2
sprinklers from the floor below floor.
Alternatively, since it seems you have water supply to be considering the
additional sprinklers required for the communicating spaces with the room
design, if you were doing .1/1500 design, would the required area of
operation not be limited to a given floor and would that extra room on the
3rd floor have more than 2 sprinklers? If the 2nd room on the 3rd floor has
only 2 sprinklers (depending on spacing/flow requirements), it may be
comparitable to the room design you may be able to justify the calc without
your friend installing auto closing doors, lintel and reducing the 12'
opening.
A lot of ifs for you.

Damien Shannon.



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina
Jr
Sent: Thursday, July 16, 2009 10:26 PM
To: SprinklerFORUM@firesprinkler.org
Cc: msingletonf...@sbcglobal.net
Subject: Room design method - Technical information

?I am trying to help a contractor friend with a residential fire sprinkler
system originally designed per NFPA-13D using Tyco 'LF-II' 4.9K.
His client has areas where the beams are spaced less than 3'-6" and are 8"
in Depth . He can not ( or does not) want to change the beam depth or
spacing if possible so I inquired with the local AHJ about changing it to a
regular NFPA-13 system and using the room design method (so as to use quick
response heads near the bottom of the beams). I got the ok for that part,
but the room configuration doesn't quite fit the code configuration. The
most remote and demanding area is a third floor room (loft?) which has two
compartments one being opened to the 2nd floor below. By reading the section
on 'Room Design Method' it appears the main concern is keeping the heat in 1
room long enough to activate all the heads in it and possibly 1 or 2 heads
near the unprotected opening. It appears that it would meet all other
aspects of the code but the only difference being that the high room area
has a 12' wide opening on the 2nd floor to an adjoin room (10' below the
high ceiling). Is there a
 ny research data on the 'Room Design Method' where the mathematics and
science required the 8" lintel and/or 8' maximum width of unprotected
opening? Any suggestions? (besides walking away from it).
 


George Medina Jr.
Sr. Fire Sprinkler Designer
95-1015 Ka'apeha Pl.
Mililani, HI 96819


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus signature
database 4252 (20090717) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 4252 (20090717) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 
 

__________ Information from ESET Smart Security, version of virus signature
database 4252 (20090717) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to