Are we still talking about a residential occupancy?

Lamar Vaughn
Vaughn & Company

---- Damien Shannon <qedsprinkl...@usa.com> wrote: 
> My understanding would be:
> NFPA 13, 2007, 11.2.3.3.5 (2) would allow 8' wide with a 8" lintel for light
> hazard Room design to be considered an unprotected opening. i.e. you could
> still use room design but would have to calc your 'design room' and 2
> sprinklers in each of the communicating spaces (that have unprotected
> openings). If the door into the other room on the 3rd floor could be
> considered 'Non-rated automatic or self closing doors' as stated in NFPA 13,
> 2007 section 11.2.3.3.5 (1), had your 8" lintel opening (opening restricted
> to 8' wide), you could calc the sprinklers in the design room and 2
> sprinklers from the floor below floor.
> Alternatively, since it seems you have water supply to be considering the
> additional sprinklers required for the communicating spaces with the room
> design, if you were doing .1/1500 design, would the required area of
> operation not be limited to a given floor and would that extra room on the
> 3rd floor have more than 2 sprinklers? If the 2nd room on the 3rd floor has
> only 2 sprinklers (depending on spacing/flow requirements), it may be
> comparitable to the room design you may be able to justify the calc without
> your friend installing auto closing doors, lintel and reducing the 12'
> opening.
> A lot of ifs for you.
> 
> Damien Shannon.
> 
> 
> 
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina
> Jr
> Sent: Thursday, July 16, 2009 10:26 PM
> To: SprinklerFORUM@firesprinkler.org
> Cc: msingletonf...@sbcglobal.net
> Subject: Room design method - Technical information
> 
> ?I am trying to help a contractor friend with a residential fire sprinkler
> system originally designed per NFPA-13D using Tyco 'LF-II' 4.9K.
> His client has areas where the beams are spaced less than 3'-6" and are 8"
> in Depth . He can not ( or does not) want to change the beam depth or
> spacing if possible so I inquired with the local AHJ about changing it to a
> regular NFPA-13 system and using the room design method (so as to use quick
> response heads near the bottom of the beams). I got the ok for that part,
> but the room configuration doesn't quite fit the code configuration. The
> most remote and demanding area is a third floor room (loft?) which has two
> compartments one being opened to the 2nd floor below. By reading the section
> on 'Room Design Method' it appears the main concern is keeping the heat in 1
> room long enough to activate all the heads in it and possibly 1 or 2 heads
> near the unprotected opening. It appears that it would meet all other
> aspects of the code but the only difference being that the high room area
> has a 12' wide opening on the 2nd floor to an adjoin room (10' below the
> high ceiling). Is there a
>  ny research data on the 'Room Design Method' where the mathematics and
> science required the 8" lintel and/or 8' maximum width of unprotected
> opening? Any suggestions? (besides walking away from it).
>  
> 
> 
> George Medina Jr.
> Sr. Fire Sprinkler Designer
> 95-1015 Ka'apeha Pl.
> Mililani, HI 96819
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> 
> __________ Information from ESET Smart Security, version of virus signature
> database 4252 (20090717) __________
> 
> The message was checked by ESET Smart Security.
> 
> http://www.eset.com
> 
> 
>  
> 
> __________ Information from ESET Smart Security, version of virus signature
> database 4252 (20090717) __________
> 
> The message was checked by ESET Smart Security.
> 
> http://www.eset.com
>  
>  
> 
> __________ Information from ESET Smart Security, version of virus signature
> database 4252 (20090717) __________
> 
> The message was checked by ESET Smart Security.
> 
> http://www.eset.com
>  
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum