There are many pockets that would require sprinklers in it and I am  
trying to utilize the code for the best possible design ( not get  
around it ). I have

Sent from my iPhone

On Jul 17, 2009, at 7:21 AM, Ron Greenman <rongreen...@gmail.com> wrote:

> I can't see the advantage of 13 room design over 13D unless you're
> looking for the better system. If it's the few extra heads because of
> the beams I don't see how that can increase costs enough to warrant
> the effort of trying to get around the rules. He chose the
> architecture. If that requires more sprinklers and he doesn't want to
> change the "look" then certain rules of the road apply. Now if he
> wants the added protection of a 13 system that's another story but if,
> as you say, it's still residential then you apply the residential
> rules of 13, not the room design rules. Am I missing something here?
>
> On Fri, Jul 17, 2009 at 7:07 AM, George Medina<fireg...@aol.com>  
> wrote:
>> We are talking about a residential occupancy still.
>>
>> Sent from my iPhone
>>
>> On Jul 17, 2009, at 5:27 AM, <lamarvau...@charter.net> wrote:
>>
>>> Are we still talking about a residential occupancy?
>>>
>>> Lamar Vaughn
>>> Vaughn & Company
>>>
>>> ---- Damien Shannon <qedsprinkl...@usa.com> wrote:
>>>> My understanding would be:
>>>> NFPA 13, 2007, 11.2.3.3.5 (2) would allow 8' wide with a 8" lintel
>>>> for light
>>>> hazard Room design to be considered an unprotected opening. i.e.
>>>> you could
>>>> still use room design but would have to calc your 'design room'  
>>>> and 2
>>>> sprinklers in each of the communicating spaces (that have  
>>>> unprotected
>>>> openings). If the door into the other room on the 3rd floor could  
>>>> be
>>>> considered 'Non-rated automatic or self closing doors' as stated in
>>>> NFPA 13,
>>>> 2007 section 11.2.3.3.5 (1), had your 8" lintel opening (opening
>>>> restricted
>>>> to 8' wide), you could calc the sprinklers in the design room and 2
>>>> sprinklers from the floor below floor.
>>>> Alternatively, since it seems you have water supply to be
>>>> considering the
>>>> additional sprinklers required for the communicating spaces with
>>>> the room
>>>> design, if you were doing .1/1500 design, would the required area  
>>>> of
>>>> operation not be limited to a given floor and would that extra room
>>>> on the
>>>> 3rd floor have more than 2 sprinklers? If the 2nd room on the 3rd
>>>> floor has
>>>> only 2 sprinklers (depending on spacing/flow requirements), it  
>>>> may be
>>>> comparitable to the room design you may be able to justify the calc
>>>> without
>>>> your friend installing auto closing doors, lintel and reducing the
>>>> 12'
>>>> opening.
>>>> A lot of ifs for you.
>>>>
>>>> Damien Shannon.
>>>>
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
>>>> George Medina
>>>> Jr
>>>> Sent: Thursday, July 16, 2009 10:26 PM
>>>> To: SprinklerFORUM@firesprinkler.org
>>>> Cc: msingletonf...@sbcglobal.net
>>>> Subject: Room design method - Technical information
>>>>
>>>> ?I am trying to help a contractor friend with a residential fire
>>>> sprinkler
>>>> system originally designed per NFPA-13D using Tyco 'LF-II' 4.9K.
>>>> His client has areas where the beams are spaced less than 3'-6" and
>>>> are 8"
>>>> in Depth . He can not ( or does not) want to change the beam  
>>>> depth or
>>>> spacing if possible so I inquired with the local AHJ about changing
>>>> it to a
>>>> regular NFPA-13 system and using the room design method (so as to
>>>> use quick
>>>> response heads near the bottom of the beams). I got the ok for that
>>>> part,
>>>> but the room configuration doesn't quite fit the code
>>>> configuration. The
>>>> most remote and demanding area is a third floor room (loft?) which
>>>> has two
>>>> compartments one being opened to the 2nd floor below. By reading
>>>> the section
>>>> on 'Room Design Method' it appears the main concern is keeping the
>>>> heat in 1
>>>> room long enough to activate all the heads in it and possibly 1 or
>>>> 2 heads
>>>> near the unprotected opening. It appears that it would meet all  
>>>> other
>>>> aspects of the code but the only difference being that the high
>>>> room area
>>>> has a 12' wide opening on the 2nd floor to an adjoin room (10'
>>>> below the
>>>> high ceiling). Is there a
>>>> ny research data on the 'Room Design Method' where the mathematics
>>>> and
>>>> science required the 8" lintel and/or 8' maximum width of  
>>>> unprotected
>>>> opening? Any suggestions? (besides walking away from it).
>>>>
>>>>
>>>>
>>>> George Medina Jr.
>>>> Sr. Fire Sprinkler Designer
>>>> 95-1015 Ka'apeha Pl.
>>>> Mililani, HI 96819
>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>>>
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>> requ...@firesprinkler.org
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> __________ Information from ESET Smart Security, version of virus
>>>> signature
>>>> database 4252 (20090717) __________
>>>>
>>>> The message was checked by ESET Smart Security.
>>>>
>>>> http://www.eset.com
>>>>
>>>>
>>>>
>>>>
>>>> __________ Information from ESET Smart Security, version of virus
>>>> signature
>>>> database 4252 (20090717) __________
>>>>
>>>> The message was checked by ESET Smart Security.
>>>>
>>>> http://www.eset.com
>>>>
>>>>
>>>>
>>>> __________ Information from ESET Smart Security, version of virus
>>>> signature
>>>> database 4252 (20090717) __________
>>>>
>>>> The message was checked by ESET Smart Security.
>>>>
>>>> http://www.eset.com
>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>>>
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>>> requ...@firesprinkler.org
>>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum-
>>> requ...@firesprinkler.org
>>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> requ...@firesprinkler.org
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: techsupp...@firesprinkler.org
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to