A fitter asked us how long a branch line has to be before it requires end of
the line restraint. A fire marshal told him he could never find an answer so
they put in place 13ft or longer. 

9.3.6.3 The end sprinkler on a line shall be restrained against excessive
vertical and lateral movement. In my opinion, the way this is written, all
branch lines are to have them, which brought up the next debate;

 

3.5.1 Branch Line - The pipes supplying sprinklers, either directly or
through sprigs, drops, return bends, or arm-overs. Would a 1x1'-0 pipe
coming from a main supplying a single sprinkler through a return bend (or
any configuration) be a branch line, and if so would it require an end of
the line restraint? The definition says a pipe supplying sprinklers so this
would qualify because an arm-over is defined as coming from a branch line.
If this is the case, I think a limit of length is required to be put on
branch lines requiring end of the line restraint. 

 