Depends on just how technical you want to get.

Based on the definition, the branch line serves multiple sprinklers.  The 
9.3.6.3 sounds like it's written more for a branch line where you've got 
uprights or pendant sprinklers connected directly to the branch line.  (exposed 
construction?)  This is supported when looking at the various illustrations 
within 13.

So are we talking about a sprinkler drop or an actual branch line?

The branch line support is defined in 9.2.3.4.1 (NFPA 13, 2007), armover is 
covered in 9.2.3.5 and sprigs in 9.2.3.7.  If you look at sprigs for instance 
the restraint requirement applies if it's over 4 ft in length.  This same 
criteria could be conversely applied to a drop to a sprinkler below.

It's all up to the AHJ when it starts getting into these gray areas.

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Thursday, July 23, 2009 8:46 AM
To: [email protected]
Subject: Branchline/Restraint of Branchline

A fitter asked us how long a branch line has to be before it requires end of 
the line restraint. A fire marshal told him he could never find an answer so 
they put in place 13ft or longer. 

9.3.6.3 The end sprinkler on a line shall be restrained against excessive 
vertical and lateral movement. In my opinion, the way this is written, all 
branch lines are to have them, which brought up the next debate;

 

3.5.1 Branch Line - The pipes supplying sprinklers, either directly or through 
sprigs, drops, return bends, or arm-overs. Would a 1x1'-0 pipe coming from a 
main supplying a single sprinkler through a return bend (or any configuration) 
be a branch line, and if so would it require an end of the line restraint? The 
definition says a pipe supplying sprinklers so this would qualify because an 
arm-over is defined as coming from a branch line.
If this is the case, I think a limit of length is required to be put on branch 
lines requiring end of the line restraint. 

 

Thank You,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to