>From what you've written it sounds as if you are going a different direction 
>than what the AHJ is requesting.  From your e-mail it appears that he is only 
>requesting sprinklers below the mezzanine, not in-racks.  

Now what he is asking for to be installed below the mezzanine is the 
"Intermediate Style" sprinkler such as the Reliable "F-1" or Viking VK550/560 
or similar with the integral steel shield.

Some of the things you are going to need before going much further are the 
temperature of the existing ceiling sprinklers and the design criteria of the 
existing ceiling sprinklers.

Looking at Table 16.2.1.3.2 and Figure 16.2.1.3.2(b), even with in-racks the 
ceiling system criteria would need to supply somewhere between .24 and 
.26/2000.  I'd be suspicious of a 5.6K design system being designed to that 
criteria.  Applying Fig. 16.2.1.3.4.1, per Table 16.2.1.3.2 at 60% of that 
(somewhere around .15) the ceiling system may work.

So what I'm saying is you need more info. 

You have two issues.  One you need to provide sprinklers below the mezzanine 
since the floor space is now shielded from the ceiling sprinklers.  That's a 
given.  Second you need to examine the need for in-rack sprinklers.  Depending 
on the performance of the ceiling system, how you classify the commodity  and 
what your design criteria will be below the mezzanine, you may or may not need 
in-racks.

 

As you would imagine, I've only spent a few minutes taking a look at this so 
there may be other potential approaches that would work.  But as time is 
limited I leave that for you to explore.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of sam b
Sent: Thursday, July 23, 2009 7:38 AM
To: [email protected]
Subject: In rack sprinklers at celing level

Hiii


I visited a warehouse (8.6 m height) which is protected by  upright sprinklers 
(K-5.6) .

Now the client have added  a steel mezzanine structure with racks above and 
below.

Now local Fire authority have asked to *provide sprinklers(in rack type) at the 
ceiling level of the mezzanine for the below racks.*

**

Racks below will be stored with electronic good items in cartons (mainly items 
for electronic panels).

Max storage height will be 4 m.

Their are 5 multiple row racks (2.4m wide and 9.3 m length) and 2 single row 
racks of 1.2 m wide and 9.3 m length). aisle width of 1.2 m between racks.



>From NFPA ,I could see only one layer rack sprinklers enough for each 
>rack
and since only 9.3 m length I need only 3 in rack sprinklers per rack.

when the sprinklers provided at ceiling Is this the correct way forward??

Can we provide In rack sprinklers at ceiling in these cases?



I am not finding it easy to locate the answer.



Any help welcome


Thaanx in advance

Sam
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to