Craig

I wil check this one.
Thaanx a lott

Sam

On Mon, Jul 27, 2009 at 4:27 PM, <[email protected]> wrote:

> Sam to answer your questions:
>
> 1. I would look at NFPA 13 and see what is the required ceiling density
> based on the rack storage scenario.  As I said, the existing ceiling system
> may or may not be compliant.   Start looking at this building as if it were
> a brand new project, define all your criteria and see what you get.  Then
> look at it based on the existing ceiling system criteria and see if there
> are any options that match that criteria.
>
> 2. The area below the grating needs sprinklers.  There's no way to avoid
> that.
>
> 3. That's a tough question without knowing what exactly you have as far as
> components.  Are these finished circuit boards or are these miscellaneous
> small parts?  If it's small parts then what are they made of?  My first
> impression would be probably class II or III but electronics can vary.
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of sam b
> Sent: Friday, July 24, 2009 4:06 PM
> To: [email protected]
>  Subject: Re: In rack sprinklers at celing level
>
> Craig
>
> As you said,  I have lost my way,
> actually the AHJ comments were little confusing for me..
> First of all they asked to
> provide sprinklers(in rack type) at the ceiling level of the mezzanine for
> the below racks. and next for some query they commented back saying inrack
> sprinklers cant b avoided.
> I think I misread that for inrack sprinklers only.(even though he mentioned
> clearly - positioned at ceiling).
> Since there was no racks at the beginning they have designed the already
> existing ceiling sprinklers @ 0.2 gpm/ft2 only.
>
> I have 3 issues now.
>
> 1. In case if we are providing  ceiling sprinklers below mezz level and
> also rack sprinklers ,Does that mean that no change in the already existing
> ceiling sprinklers be required?
>
> 2.."""One you need to provide sprinklers below the mezzanine since the
> floor space is now shielded from the ceiling sprinklers."""" IS this
> applicable if the mezz is of grating type steel constrctn(means floor space
> is not fully sheilded from ceiling sprinklers)?
> In other wrds, can we avoid ceiling sprinkelrs below mezz level and go with
> only inrack sprinklers?
>
>  3.which commodity class can electronic goods(for scada panels)packed in
> cartons  be considered?
>
>
> Sam
>
>
>
>
> On Thu, Jul 23, 2009 at 5:03 PM, <[email protected]> wrote:
>
> > >From what you've written it sounds as if you are going a different
> > direction than what the AHJ is requesting.  From your e-mail it
> > appears that he is only requesting sprinklers below the mezzanine, not
> in-racks.
> >
> > Now what he is asking for to be installed below the mezzanine is the
> > "Intermediate Style" sprinkler such as the Reliable "F-1" or Viking
> > VK550/560 or similar with the integral steel shield.
> >
> > Some of the things you are going to need before going much further are
> > the temperature of the existing ceiling sprinklers and the design
> > criteria of the existing ceiling sprinklers.
> >
> > Looking at Table 16.2.1.3.2 and Figure 16.2.1.3.2(b), even with
> > in-racks the ceiling system criteria would need to supply somewhere
> > between .24 and .26/2000.  I'd be suspicious of a 5.6K design system
> > being designed to that criteria.  Applying Fig. 16.2.1.3.4.1, per
> > Table 16.2.1.3.2 at 60% of that (somewhere around .15) the ceiling system
> may work.
> >
> > So what I'm saying is you need more info.
> >
> > You have two issues.  One you need to provide sprinklers below the
> > mezzanine since the floor space is now shielded from the ceiling
> sprinklers.
> >  That's a given.  Second you need to examine the need for in-rack
> > sprinklers.  Depending on the performance of the ceiling system, how
> > you classify the commodity  and what your design criteria will be
> > below the mezzanine, you may or may not need in-racks.
> >
> >
> >
> > As you would imagine, I've only spent a few minutes taking a look at
> > this so there may be other potential approaches that would work.  But
> > as time is limited I leave that for you to explore.
> >
> >
> >
> > Craig L. Prahl, CET
> > Fire Protection Specialist
> > Mechanical Department
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> > 864.599.8439 [email protected] http://www.ch2m.com
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of sam b
> > Sent: Thursday, July 23, 2009 7:38 AM
> > To: [email protected]
> > Subject: In rack sprinklers at celing level
> >
> > Hiii
> >
> >
> > I visited a warehouse (8.6 m height) which is protected by  upright
> > sprinklers (K-5.6) .
> >
> > Now the client have added  a steel mezzanine structure with racks
> > above and below.
> >
> > Now local Fire authority have asked to *provide sprinklers(in rack
> > type) at the ceiling level of the mezzanine for the below racks.*
> >
> > **
> >
> > Racks below will be stored with electronic good items in cartons
> > (mainly items for electronic panels).
> >
> > Max storage height will be 4 m.
> >
> > Their are 5 multiple row racks (2.4m wide and 9.3 m length) and 2
> > single row racks of 1.2 m wide and 9.3 m length). aisle width of 1.2 m
> > between racks.
> >
> >
> >
> > >From NFPA ,I could see only one layer rack sprinklers enough for each
> > >rack
> > and since only 9.3 m length I need only 3 in rack sprinklers per rack.
> >
> > when the sprinklers provided at ceiling Is this the correct way forward??
> >
> > Can we provide In rack sprinklers at ceiling in these cases?
> >
> >
> >
> > I am not finding it easy to locate the answer.
> >
> >
> >
> > Any help welcome
> >
> >
> > Thaanx in advance
> >
> > Sam
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%3ASprinklerforum-reques
> > [email protected]> (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%3ASprinklerforum-reques
>  > [email protected]> (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to