ESFR's are very limited, averaging the height is not allowed. There is
also a 20 ft maximum limit for distance from the top of storage to the
roof sprinklers but I don't know if applies when there are in-rack
sprinklers.

Ron Fletcher
Aero Automatic Phoenix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, July 29, 2009 1:27 PM
To: sprinklerforum: firesprinkler.org
Subject: 54' High Warehouse

Hello Forumites,

 I'm looking at a warehouse with pallet rack storage of class iv
commodities to
25 ft. in a pre-engineered building with an eave height of 34 ft. and a
ridge
of 54 ft.(2" in 12" slope).Table 12.3.2.3.1 (2002) indicates a maximum
roof height of 45 ft.My question is ,can I average the roof height to
stay
within the table limits,or is "ESFR" out of the possibilities?Is there
any other
way to satisfy the roof height issue?

Thanks for the Help,
Lamar Vaughn,SET
Vaughn and Company
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to