My reply would be to do one of two things. 1) install a flat non-comb. Drop ceiling at the 34'height 2) Pay for a FPE to spec./design and seal the drawings for the building as built.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Fletcher, Ron Sent: Wednesday, July 29, 2009 2:41 PM To: [email protected] Subject: RE: 54' High Warehouse ESFR's are very limited, averaging the height is not allowed. There is also a 20 ft maximum limit for distance from the top of storage to the roof sprinklers but I don't know if applies when there are in-rack sprinklers. Ron Fletcher Aero Automatic Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, July 29, 2009 1:27 PM To: sprinklerforum: firesprinkler.org Subject: 54' High Warehouse Hello Forumites, I'm looking at a warehouse with pallet rack storage of class iv commodities to 25 ft. in a pre-engineered building with an eave height of 34 ft. and a ridge of 54 ft.(2" in 12" slope).Table 12.3.2.3.1 (2002) indicates a maximum roof height of 45 ft.My question is ,can I average the roof height to stay within the table limits,or is "ESFR" out of the possibilities?Is there any other way to satisfy the roof height issue? Thanks for the Help, Lamar Vaughn,SET Vaughn and Company _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)