Although not an ESFR issue, clearance on spray sprinklers is  
restricted.  It underwent a huge improvement during this ROP/ROC  
cycle.  It varies by commodity class, storage arrangement, and height.  
For instance, Class I-IV in racks: up to 25 ft is treated differently  
than greater than 25 ft.  Although not a simple one size fits all, it  
is very explicit so most will come up with the same answers.

Roland

On Jul 29, 2009, at 1:41 PM, Fletcher, Ron wrote:

> ESFR's are very limited, averaging the height is not allowed. There is
> also a 20 ft maximum limit for distance from the top of storage to the
> roof sprinklers but I don't know if applies when there are in-rack
> sprinklers.
>
> Ron Fletcher
> Aero Automatic Phoenix

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to