Although not an ESFR issue, clearance on spray sprinklers is restricted. It underwent a huge improvement during this ROP/ROC cycle. It varies by commodity class, storage arrangement, and height. For instance, Class I-IV in racks: up to 25 ft is treated differently than greater than 25 ft. Although not a simple one size fits all, it is very explicit so most will come up with the same answers.
Roland On Jul 29, 2009, at 1:41 PM, Fletcher, Ron wrote: > ESFR's are very limited, averaging the height is not allowed. There is > also a 20 ft maximum limit for distance from the top of storage to the > roof sprinklers but I don't know if applies when there are in-rack > sprinklers. > > Ron Fletcher > Aero Automatic Phoenix _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)