NFPA 25, Section 8.3.5 does not require comparison over a 4 year period but 
does require comparison to the original acceptance test (which should match the 
factory curve) and/or name plate data.  If the pressure at rated flow is less 
than 95% of the acceptance test or nameplate data, an investigation into cause 
is warranted.
 
I have clients who ask me to review the pump test results.  Sometimes the 
contractor offers an opinion on performance and sometimes not.  25 does not 
explicitly require the contractor to do the analysis.  If you run the test and 
see a degradation in performance of 5% or more, it would be prudent to notify 
the owner that there may be maintenance issues that need investigation.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Fri, 8/28/09, Bobby McCullough <[email protected]> wrote:


From: Bobby McCullough <[email protected]>
Subject: Fire Pump Test Results
To: [email protected]
Date: Friday, August 28, 2009, 10:51 AM


Does anyone know if it is a NFPA or code requirement to compare the test
results of fire pumps over a four year period?  I've been using a spread
sheet to compare the current test with the original acceptance test
(rarely available) and with previous tests.  I'm finding what may be
concerns and I would like to provide a code reference to the owner.



Thank you!



Bobby McCullough

Atlanta Sprinkler Inspection

[email protected]





Some days (like today) you guys provide some great humor.  Thanks again.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to