I downloaded a four year comparison from the Oklahoma State University website (www.osufiret.com) months ago and started comparing results. I couldn't find any requirements in NFPA 25 and wondered if it was elsewhere.
Thanks again. Bobby -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David de Vries Sent: Friday, August 28, 2009 12:15 PM To: [email protected] Subject: Re: Fire Pump Test Results NFPA 25, Section 8.3.5 does not require comparison over a 4 year period but does require comparison to the original acceptance test (which should match the factory curve) and/or name plate data. If the pressure at rated flow is less than 95% of the acceptance test or nameplate data, an investigation into cause is warranted. I have clients who ask me to review the pump test results. Sometimes the contractor offers an opinion on performance and sometimes not. 25 does not explicitly require the contractor to do the analysis. If you run the test and see a degradation in performance of 5% or more, it would be prudent to notify the owner that there may be maintenance issues that need investigation. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated --- On Fri, 8/28/09, Bobby McCullough <[email protected]> wrote: From: Bobby McCullough <[email protected]> Subject: Fire Pump Test Results To: [email protected] Date: Friday, August 28, 2009, 10:51 AM Does anyone know if it is a NFPA or code requirement to compare the test results of fire pumps over a four year period? I've been using a spread sheet to compare the current test with the original acceptance test (rarely available) and with previous tests. I'm finding what may be concerns and I would like to provide a code reference to the owner. Thank you! Bobby McCullough Atlanta Sprinkler Inspection [email protected] Some days (like today) you guys provide some great humor. Thanks again. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum