I am working on a warehouse which presently has very inadequate 
protection. One of the improvements needed is a fire pump. I have two 
options: a 1500 at 95 or a 2000 at 80. We can't go over the 95 psi or 
we end up with a churn pressure over 175 psi. However, the flow drops 
to 20 psi at 2400 gpm. The ESFR system I am recommending requires 
about 1950 gpm, including hose streams (the fire pump will have to 
supply hose streams as well). I want to use the 2000 gpm pump because 
it gives me better hydraulics, however, I can't test to 150% flow. 
NFPA 25 says "If available suction supplies do not allow flowing of 
150 percent of the rated pump capacity, the fire pump shall be 
permitted to operate at maximum allowable discharge." Has anyone 
successfully presented this to an insurance company and Fire Marshal 
on a new installation and got them to go along? Any hints on how to present it?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  