I realize this scenario is in light hazard, but remember if you do this in
OH areas a lot of the EC sprinklers are standard response over 16x16 so at
that point be careful what you mix, so you don't mix standard and quick.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Monday, August 31, 2009 9:28 PM
To: [email protected]
Subject: Re: Mixing sprinkler heads types - EC and standard

Thanks Cliff and Todd,

Yes, the area is light hazard and they will all be QR rated.  I was
questioned about mixing but did not see anything in either the sprk head
listing or 13 that didn't allow them.  I like the idea of different thread
sizes since that was one item brought up during our discussion and how to
handle it when replacement time came. Now to go look and see what my options
are.

Again, thank you!!

Richard
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to