I don't recall seeing anything but 14x14 (in OH) and 16x16, 18x18, and 20x20
EC spacing increments. If you need 15x15, you'll have to round up to 16x16.

Don't forget that if you're in LH, you need to consider if you'll end up
flowing more heads with the EC requirement to flow a min of 5, vrs using
room design or 900 SF (vrs 5 EC's at 400=2,000!).

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Monday, August 31, 2009 8:55 PM
To: sprinklerforum
Subject: Mixing sprinkler heads types - EC and standard

Is it ok to have a mix of EC and standard heads in a space?  Say you are
laying out a space that for purposes of discussion are mostly 20x20 bays.
Using an EC at 20x20 throw means one per bay.  Now off to the side, we have
smaller areas, say 14x14 in size.  Can I spec a standard head of max throw
of 15x15 or should I continue using EC heads in these smaller spaces?

thanks,

Richard