NFPA 16, 2007 edition say's 5.14* Test Connections. System test connections shall be sized to accommodate both the low flow of the proportioner and the maximum anticipated flow through the proportioner.(Also see A5.14)
Then some special requirements appear in chapter 8 8.4.1.4.4 For balanced pressure and positive pressure proportioning systems, flow tests shall be permitted to be conducted through the test connections required in Section 5.13. For other proportioning system types, full-flow testing of system and discharge devices is required to properly evaluate the proportioning system. So the answer is generally yes, but if your system is not a balanced or positive pressure proportioning system full flow testing is required, I'm guessing thru the system? Anyone out there on the 16 committee? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Tuesday, September 01, 2009 5:19 AM To: [email protected] Subject: Foam test connection I am a bit confused on the test connection for a foam-water sprinkler system. Does it only have to satisfy the minimum flow of the 4 most remote sprinklers or does it also have accommodate the anticipated maximum flow through the proportioner? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)