I have a balanced pressure system.  What confused me was that 5.13 is
about supervision not testing.
I got in touch with the manufacture and they felt it would only be
necessary to test the 4 head flow since the 
proportioners typically have trouble getting the correct mix at low
flows. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
McMahon
Sent: Wednesday, September 02, 2009 10:22 AM
To: [email protected]
Subject: RE: Foam test connection

NFPA 16, 2007 edition say's

5.14* Test Connections. System test connections shall be sized to
accommodate both the low flow of the proportioner and the maximum
anticipated flow through the proportioner.(Also see A5.14)

Then some special requirements appear in chapter 8

8.4.1.4.4 For balanced pressure and positive pressure proportioning
systems, flow tests shall be permitted to be conducted through the test
connections required in Section 5.13. For other proportioning system
types, full-flow testing of system and discharge devices is required to
properly evaluate the proportioning system.

So the answer is generally yes, but if your system is not a balanced or
positive pressure proportioning system full flow testing is required,
I'm guessing thru the system?

Anyone out there on the 16 committee?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Tuesday, September 01, 2009 5:19 AM
To: [email protected]
Subject: Foam test connection

I am a bit confused on the test connection for a foam-water sprinkler
system.  
Does it only have to satisfy the minimum flow of the 4 most remote
sprinklers or does it also have accommodate the anticipated maximum flow
through the proportioner?
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to