Thanks Craig, but more qualification of the question again. Does there
need to be some identification at the transformer denoting that a
feeder goes to a fire pump so it won't be inadvertently disconnected.
The reference you sent seems to only apply at disconnect locations.

On Thu, Sep 3, 2009 at 1:10 PM, <[email protected]> wrote:
> Article 695 of NFPA 70 (NEC) covers Fire Pumps.  2008 ed, See 695.3(1),  
> refers to 230.2, & NFPA 20:9.2.3
>
> 230.2(E) Identification. Where a building or structure is supplied
> by more than one service, or any combination of
> branch circuits, feeders, and services, a permanent plaque
> or directory shall be installed at each service disconnect
> location denoting all other services, feeders, and branch
> circuits supplying that building or structure and the area
> served by each. See 225.37.
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, September 03, 2009 3:43 PM
> To: [email protected]
> Subject: Marking of Feeders
>
> When a transformer is supplying a fire pump and other services do the fire 
> pump feeders need to be marked and if so what reference?
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to