There are numerous references to Identification of Conductors throughout the 
NEC.  The electrical guy needs to determine what and how based on the specific 
reference.  Sorry but I just don't have time to go through them all right now.  
Look at Article 215 FEEDERS, 

215.12 Identification for Feeders.
(A) Grounded Conductor. The grounded conductor of a
feeder shall be identified in accordance with 200.6.
(B) Equipment Grounding Conductor. The equipment
grounding conductor shall be identified in accordance with
250.119.
(C) Ungrounded Conductors. Where the premises wiring
system has feeders supplied from more than one nominal
voltage system, each ungrounded conductor of a feeder
shall be identified by phase or line and system at all termination,
connection, and splice points. The means of identification
shall be permitted to be by separate color coding,
marking tape, tagging, or other approved means. The
method utilized for conductors originating within each
feeder panel board or similar feeder distribution equipment
shall be documented in a manner that is readily available or
shall be permanently posted at each feeder panel board or
similar feeder distribution equipment.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, September 03, 2009 4:15 PM
To: [email protected]
Subject: Re: Marking of Feeders

Thanks Craig, but more qualification of the question again. Does there need to 
be some identification at the transformer denoting that a feeder goes to a fire 
pump so it won't be inadvertently disconnected.
The reference you sent seems to only apply at disconnect locations.

On Thu, Sep 3, 2009 at 1:10 PM, <[email protected]> wrote:
> Article 695 of NFPA 70 (NEC) covers Fire Pumps.  2008 ed, See 
> 695.3(1),  refers to 230.2, & NFPA 20:9.2.3
>
> 230.2(E) Identification. Where a building or structure is supplied by 
> more than one service, or any combination of branch circuits, feeders, 
> and services, a permanent plaque or directory shall be installed at 
> each service disconnect location denoting all other services, feeders, 
> and branch circuits supplying that building or structure and the area 
> served by each. See 225.37.
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [email protected] http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron 
> Greenman
> Sent: Thursday, September 03, 2009 3:43 PM
> To: [email protected]
> Subject: Marking of Feeders
>
> When a transformer is supplying a fire pump and other services do the fire 
> pump feeders need to be marked and if so what reference?
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to