Thanks Craig.

I'm on vacation, was asked a question and don't have many of my
references handy. I thought I's ask you guys since you all seem to
know a little bit about this stuff. As is always the case, any help is
appreciated muy mucho.

On Thu, Sep 3, 2009 at 1:34 PM, <[email protected]> wrote:
> There are numerous references to Identification of Conductors throughout the 
> NEC.  The electrical guy needs to determine what and how based on the 
> specific reference.  Sorry but I just don't have time to go through them all 
> right now.  Look at Article 215 FEEDERS,
>
> 215.12 Identification for Feeders.
> (A) Grounded Conductor. The grounded conductor of a
> feeder shall be identified in accordance with 200.6.
> (B) Equipment Grounding Conductor. The equipment
> grounding conductor shall be identified in accordance with
> 250.119.
> (C) Ungrounded Conductors. Where the premises wiring
> system has feeders supplied from more than one nominal
> voltage system, each ungrounded conductor of a feeder
> shall be identified by phase or line and system at all termination,
> connection, and splice points. The means of identification
> shall be permitted to be by separate color coding,
> marking tape, tagging, or other approved means. The
> method utilized for conductors originating within each
> feeder panel board or similar feeder distribution equipment
> shall be documented in a manner that is readily available or
> shall be permanently posted at each feeder panel board or
> similar feeder distribution equipment.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, September 03, 2009 4:15 PM
> To: [email protected]
> Subject: Re: Marking of Feeders
>
> Thanks Craig, but more qualification of the question again. Does there need 
> to be some identification at the transformer denoting that a feeder goes to a 
> fire pump so it won't be inadvertently disconnected.
> The reference you sent seems to only apply at disconnect locations.
>
> On Thu, Sep 3, 2009 at 1:10 PM, <[email protected]> wrote:
>> Article 695 of NFPA 70 (NEC) covers Fire Pumps.  2008 ed, See
>> 695.3(1),  refers to 230.2, & NFPA 20:9.2.3
>>
>> 230.2(E) Identification. Where a building or structure is supplied by
>> more than one service, or any combination of branch circuits, feeders,
>> and services, a permanent plaque or directory shall be installed at
>> each service disconnect location denoting all other services, feeders,
>> and branch circuits supplying that building or structure and the area
>> served by each. See 225.37.
>>
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Specialist
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
>> 864.599.8439 [email protected] http://www.ch2m.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron
>> Greenman
>> Sent: Thursday, September 03, 2009 3:43 PM
>> To: [email protected]
>> Subject: Marking of Feeders
>>
>> When a transformer is supplying a fire pump and other services do the fire 
>> pump feeders need to be marked and if so what reference?
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to