Why not?  I installed Tyco ECOH heads in a fire station in Myrtle Beach, and
there were no issues with them.  There's nothing in the listing the
specifically excludes them from that use.

On Tue, Sep 15, 2009 at 12:40 PM, Ed Kramer <[email protected]> wrote:

> I need a reality check:  Section 8.4.2 (07) addresses sidewall sprinklers
> and states sidewall sprinks can be installed to protect areas beneath OH
> doors.
>
>
>
> Section 8.4.3 addresses extended coverage sprinklers and doesn't mention OH
> doors.
>
>
>
> I interpret the above to mean that standard coverage sidewall sprinks can
> be
> installed beneath OH doors, but extended coverage sidewall sprinks can't.
> Correct?
>
>
>
> Ed Kramer
>
> Littleton, CO
>