Ed, What this section is allowing us to do is install, in most cases dependent on door size, one standard spray SW sprinkler under an OH door using light hazard spacing in an otherwise OH occupancy. For example, an OH door that is 14 x 12 using OH spacing of 130 sf would require 2 sidewalls, but using LH spacing of 196 sf one sprinkler can be installed. The use of LH ECSW's is not allowed, but the use of OH ECSW's is ok. The sprinkler will need to have a listing for ECOH in order to be used, and there are manufactures with this listing as Ben stated in his posting.
Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ed Kramer Sent: Tuesday, September 15, 2009 10:40 AM To: [email protected] Subject: sidewall sprinks under OH doors I need a reality check: Section 8.4.2 (07) addresses sidewall sprinklers and states sidewall sprinks can be installed to protect areas beneath OH doors. Section 8.4.3 addresses extended coverage sprinklers and doesn't mention OH doors. I interpret the above to mean that standard coverage sidewall sprinks can be installed beneath OH doors, but extended coverage sidewall sprinks can't. Correct? Ed Kramer Littleton, CO _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) -------------- next part -------------- No virus found in this outgoing message. Checked by AVG - www.avg.com Version: 8.5.409 / Virus Database: 270.13.100/2373 - Release Date: 09/15/09 13:37:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)