Section 8.4.3 states "Extended coverage sprinklers shall only be installed
as follows:".  The 4 items that follow it don't include OH doors.  Am I
being too literal (again!)?

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Ben Young
> Sent: Tuesday, September 15, 2009 10:46 AM
> To: [email protected]
> Subject: Re: sidewall sprinks under OH doors
> 
> Why not?  I installed Tyco ECOH heads in a fire station in Myrtle Beach,
> and
> there were no issues with them.  There's nothing in the listing the
> specifically excludes them from that use.
> 
> On Tue, Sep 15, 2009 at 12:40 PM, Ed Kramer <[email protected]> wrote:
> 
> > I need a reality check:  Section 8.4.2 (07) addresses sidewall
> sprinklers
> > and states sidewall sprinks can be installed to protect areas beneath
> OH
> > doors.
> >
> >
> >
> > Section 8.4.3 addresses extended coverage sprinklers and doesn't
> mention OH
> > doors.
> >
> >
> >
> > I interpret the above to mean that standard coverage sidewall sprinks
> can
> > be
> > installed beneath OH doors, but extended coverage sidewall sprinks
> can't.
> > Correct?
> >
> >
> >
> > Ed Kramer
> >
> > Littleton, CO
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to