I believe that was the Reliable ZX.  It was like a cross between the Omega
and the previous central institutional heads.  If I recall correctly, the
stopped making it because it had so many parts, and was too expensive to
make.  They called it their 'Cadillac' of sprinklers.

Yes, here it is:
http://www.reliablesprinkler.com/sprinklers_products.php?cid=5
You can find it halfway down the page or so in the middle column.
Apparently they only sell it overseas now.

-Ben

On Thu, Sep 17, 2009 at 4:29 PM, David de Vries <[email protected]>wrote:

> Yes, there are still plenty of Omegas and the other Central o-ring
> sprinklers out there.
>
> Tested new, they are supposed to open at 5 psi; used ones like the 50 year
> old samples sent to UL are supposed to operate at 7 psi.  Among the o-ring
> sprinklers, there were reported failures as high as 70 psi, I believe.  UL
> reported ones in the lab that did not open at 40+ psi.  Not common, but a
> few anyhow.  If you are the one in a hotel room with only one sprinkler and
> it is one of those 40+, you might have a problem in a fire.
>
> BTW there was a model by RASCO that at first glance looked a lot like an
> Omega.  I do not think the RASCO had any problem.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
> 2715 Harrison St.
> Evanston, IL 60201
> Tel: 847-733-0944
> Fax: 847-866-6255
>
>
>
> --- On Thu, 9/17/09, Autry, David <[email protected]> wrote:
>
>
> From: Autry, David <[email protected]>
> Subject: RE: Chewable topic.....Omegas
> To: "[email protected]" <[email protected]>
> Date: Thursday, September 17, 2009, 10:11 AM
>
>
> If I remember correctly, the Omegas wouldn't open at 7 psi. The one I set
> off from my collection seems to stick on the o-ring, but otherwise worked
> fine. If you only have 7 psi on your sprinklers, you've got bigger problems
> than "sticky" o-rings. (see sawmill from yesterday's post)
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
> ** Note new email address: [email protected]
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ben Young
> Sent: Thursday, September 17, 2009 10:00 AM
> To: [email protected]
> Subject: Re: Chewable topic.....Omegas
>
> When I worked in Raleigh, we pulled some out of the basement of a church
> downtown.  This was during a renovation of the basement space to turn it
> into a donation center, so it wasn't like they were only doing this because
> they were Omegas.  I managed to snag four from the dumpster for my
> collection.  The one that I set off with a lighter did manage to pop open,
> which was nice to know.  This was a little over three years ago now.
>
> The other interesting thing about this church was that they had sprinkler
> protection in the steeple, and instead of using an antifreeze or small dry
> system, they opted to use a non-listed recirculation pump to keep the
> piping
> from freezing during the winter.
> The amazing thing is that the city of Raleigh inspectors allowed this.  If
> you ever have the pleasure of working in Raleigh, you will know why that
> is.
>
> -Ben
>
> On Thu, Sep 17, 2009 at 10:26 AM, Ron Greenman <[email protected]
> >wrote:
>
> > We have eleven in the college where I work in an otherwise
> > unsprinklered building. Four are along a wall in an office. They used
> > to "protect" an opening/pass thru. The other seven are on one side of
> > a double door that opens into the public side of the financial aid
> > office. They used to "protect" something else also but I need to start
> > working and the story is long and rambling.  You are saved by the
> > bell.
> >
> > On Thu, Sep 17, 2009 at 6:24 AM, Chris Cahill <[email protected]>
> > wrote:
> > > For a small company we find them often enough.  Maybe a new site every
> > > couple weeks.  Then there are a bunch of regulars that elected not to
> > > replace.
> > >
> > > Chris Cahill, P.E.
> > > Fire Protection Engineer
> > > Sentry Fire Protection, Inc.
> > >
> > > 763-658-4483
> > > 763-658-4921 fax
> > >
> > > Email: [email protected]
> > >
> > > Mail: P.O. Box 69
> > >        Waverly, MN 55390
> > >
> > > Location: 4439 Hwy 12 SW
> > >              Waverly, MN 55390
> > > -----Original Message-----
> > > From: [email protected]
> > > [mailto:[email protected]] On Behalf Of Todd
> > Williams
> > > Sent: Thursday, September 17, 2009 8:08 AM
> > > To: [email protected]
> > > Subject: Chewable topic.....Omegas
> > >
> > > I walked into a school to do a small consulting job regarding
> > > obstructions and discovered that they still had Omega sprinklers
> > > installed. (My immediate sarcastic reaction was that since there is a
> > > good chance the Omegas may not work, do the drain pipes really cause
> > > an obstruction?) How many of you out there are still finding Omegas
> > > installed? Any statistics on how many were sold vs. how many were
> > > replaced under the program?
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > For Technical Assistance, send an email to: [email protected]
> > >
> > > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering
> > Bates Technical College
> > Tacoma, WA
> >
> > Member:
> > SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> <to%[email protected]<to%[email protected]>
> >
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to