And I still have one hospital that has had at least 2 remodels since I 
informed them of the ME-1 recall 5 years ago.  But we are gaining, last year 
we replaced all of the ME 1 in a day care and the year before, we replace 
all of the ME1 in a nursing home. And we made more than if the recall was 
done on a timely basis.

Douglas Hicks
General Fire Equipment co of Eastern Oregon, Inc
----- Original Message ----- 
From: "David de Vries" <[email protected]>
To: <[email protected]>
Sent: Thursday, September 17, 2009 1:29 PM
Subject: RE: Chewable topic.....Omegas


Yes, there are still plenty of Omegas and the other Central o-ring 
sprinklers out there.

Tested new, they are supposed to open at 5 psi; used ones like the 50 year 
old samples sent to UL are supposed to operate at 7 psi. Among the o-ring 
sprinklers, there were reported failures as high as 70 psi, I believe. UL 
reported ones in the lab that did not open at 40+ psi. Not common, but a few 
anyhow. If you are the one in a hotel room with only one sprinkler and it is 
one of those 40+, you might have a problem in a fire.

BTW there was a model by RASCO that at first glance looked a lot like an 
Omega. I do not think the RASCO had any problem.

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated
2715 Harrison St.
Evanston, IL 60201
Tel: 847-733-0944
Fax: 847-866-6255



--- On Thu, 9/17/09, Autry, David <[email protected]> wrote:


From: Autry, David <[email protected]>
Subject: RE: Chewable topic.....Omegas
To: "[email protected]" <[email protected]>
Date: Thursday, September 17, 2009, 10:11 AM


If I remember correctly, the Omegas wouldn't open at 7 psi. The one I set 
off from my collection seems to stick on the o-ring, but otherwise worked 
fine. If you only have 7 psi on your sprinklers, you've got bigger problems 
than "sticky" o-rings. (see sawmill from yesterday's post)

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ben Young
Sent: Thursday, September 17, 2009 10:00 AM
To: [email protected]
Subject: Re: Chewable topic.....Omegas

When I worked in Raleigh, we pulled some out of the basement of a church
downtown. This was during a renovation of the basement space to turn it
into a donation center, so it wasn't like they were only doing this because
they were Omegas. I managed to snag four from the dumpster for my
collection. The one that I set off with a lighter did manage to pop open,
which was nice to know. This was a little over three years ago now.

The other interesting thing about this church was that they had sprinkler
protection in the steeple, and instead of using an antifreeze or small dry
system, they opted to use a non-listed recirculation pump to keep the piping
from freezing during the winter.
The amazing thing is that the city of Raleigh inspectors allowed this. If
you ever have the pleasure of working in Raleigh, you will know why that is.

-Ben

On Thu, Sep 17, 2009 at 10:26 AM, Ron Greenman <[email protected]>wrote:

> We have eleven in the college where I work in an otherwise
> unsprinklered building. Four are along a wall in an office. They used
> to "protect" an opening/pass thru. The other seven are on one side of
> a double door that opens into the public side of the financial aid
> office. They used to "protect" something else also but I need to start
> working and the story is long and rambling. You are saved by the
> bell.
>
> On Thu, Sep 17, 2009 at 6:24 AM, Chris Cahill <[email protected]>
> wrote:
> > For a small company we find them often enough. Maybe a new site every
> > couple weeks. Then there are a bunch of regulars that elected not to
> > replace.
> >
> > Chris Cahill, P.E.
> > Fire Protection Engineer
> > Sentry Fire Protection, Inc.
> >
> > 763-658-4483
> > 763-658-4921 fax
> >
> > Email: [email protected]
> >
> > Mail: P.O. Box 69
> > Waverly, MN 55390
> >
> > Location: 4439 Hwy 12 SW
> > Waverly, MN 55390
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Todd
> Williams
> > Sent: Thursday, September 17, 2009 8:08 AM
> > To: [email protected]
> > Subject: Chewable topic.....Omegas
> >
> > I walked into a school to do a small consulting job regarding
> > obstructions and discovered that they still had Omega sprinklers
> > installed. (My immediate sarcastic reaction was that since there is a
> > good chance the Omegas may not work, do the drain pipes really cause
> > an obstruction?) How many of you out there are still finding Omegas
> > installed? Any statistics on how many were sold vs. how many were
> > replaced under the program?
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to