While we are on the subject,

 

(2002) 12.3.2.2 covers valve inspections. (2) states "Properly sealed,
locked, or supervised."

 

Case and point, during recent inspections of college dorms, I came across
several systems with nothing, several with a lock, and several with tampers.
Valves in question are the 2" ball valves that come with a 2" backflow. If
there is a lock, I put a yes to the question of supervision. If nothing, I
list no. When I price, I do so knowing that life safety mandates Electrical
supervision on a required system, which comes out to be a several hundred
more than a lock. Owner asked about providing a lock on each, I tell the
owner as long as I see it is supervised per NFPA #25, I will answer yes.

 

Comments??

 

 

 